Viewing a thread - How many BTUs to heat shop... (2) Posted 9/28/2018 20:12 (#7014692)
Subject: How many BTUs to heat shop...

Fletcher, OH

with forced air (such as hanging Reznor)?

30x48x12'8"
Dayton, OH region
Propane
Walls insulated to R13
Ceiling insulated to R48
Generally only need to keep inside temp to 45-50* to stop tool rusting
Would be nice to push temp to 60* when working inside when outside is 15* but not very often.
Would likely install two furnaces on separate thermostats in opposite corners, so one would come on at a lower setting. Second come on when first cant keep up.
This is a previously finished shop so floor heat is out of the question and not interested in radiant(ceiling height is barely enough for equipment)

ksfarmboy1960
Viewing a thread - How many BTUs to heat shop... (5)
Viewing a thread - How many BTUs to heat shop... (6) Posted 9/28/2018 21:23 (#7014880 - in reply to #7014692)
Subject: RE: How many BTUs to heat shop...

Viewing a thread - How many BTUs to heat shop... (7)
66524

Rule of thumb is 30 BTUH /sq,/foot with good tight doors and windows. Infiltration ( air leakage ) is typical your biggest heat loss due to crappy over head doors or poor or no wind barrier in walls and ceiling. 30x30X48=43200 BTUH . 100,000 furnace with 80% efficiency will give you 80,000 BTUH output. I would recommend a 90% ++ upflow furnace mounted on a wall bracket 4' or 5' above the floor .put a metal plenum on the top and blow the air high horzontally.A short return duct from the bottom to the floor to pull the cold air off the floor otherwise the heat will stratify. Hot ceiling and cold floor. Use one high efficency 90% ++ upflow furnace . The furnace will need to drain to a non freeze drain as it makes water and vents out with PVC for the flue. Unit heaters like Rezor ,you mentioned are high price for what you get and unless you buy a 90% ++ and then they are higher yet . You will still have stratification and cold floors either way with a unit heater. Usually higher efficiency will pay for itself in 5 to 10 years in fuel savings or less.
Just my opinion after being a HVAC contractor for 45 years
GOOD LUCK
Turbo 8820
Viewing a thread - How many BTUs to heat shop... (10)
Viewing a thread - How many BTUs to heat shop... (11) Posted 9/28/2018 21:37 (#7014909 - in reply to #7014692)
Subject: RE: How many BTUs to heat shop...

S.E. Washington

125,000 BTUs should do it. I base that on the fact that my friend has that size furnace in a similar size shop to yours, and we have a similar winter temperature and his shop is nice to work in.
Should be a heating company near you who can give more precise estimate for your needs. Just giving an example. I am no expert, but I don't like to be cold! Edit to add, I put a 350,000 BTU furnace in our 50x80x20 and it's a little over kill, but it's sure nice.

Edited by Turbo 8820 9/28/2018 21:45

Herbie56
Viewing a thread - How many BTUs to heat shop... (14)
Viewing a thread - How many BTUs to heat shop... (15) Posted 9/28/2018 22:37 (#7015014 - in reply to #7014692)
Subject: RE: How many BTUs to heat shop...

Coles County, Illinois

I think 125,000 will do it but with 13' walls heat stratification will be a problem with forced air. Need some way to bring hot air near ceiling back down to floor.
WTW
Viewing a thread - How many BTUs to heat shop... (18)
Viewing a thread - How many BTUs to heat shop... (19) Posted 9/28/2018 23:23 (#7015048 - in reply to #7014909)
Subject: RE: How many BTUs to heat shop...

Winkler, Manitoba Canada

Turbo 8820 - 9/28/2018 20:37

125,000 BTUs should do it. I base that on the fact that my friend has that size furnace in a similar size shop to yours, and we have a similar winter temperature and his shop is nice to work in.
Should be a heating company near you who can give more precise estimate for your needs. Just giving an example. I am no expert, but I don't like to be cold! Edit to add, I put a 350,000 BTU furnace in our 50x80x20 and it's a little over kill, but it's sure nice.

I hope that furnace does not run very much to keep your shop warm. We heat 50x76x18 with 10kw, about 35000 BTU.

Edited by WTW 9/29/2018 00:31

justworking
Viewing a thread - How many BTUs to heat shop... (22)
Viewing a thread - How many BTUs to heat shop... (23) Posted 9/28/2018 23:42 (#7015061 - in reply to #7014692)
Subject: RE: How many BTUs to heat shop...WWW.DIRECTPIVOTPARTS.COM
JUST BOUGHT A TUBE HEATER FROM WWW.DIRECTPIVOTPARTS.COM I SEEN THEY HAD FORCED AIR HANGING HEATER TOO
Phred
Viewing a thread - How many BTUs to heat shop... (26)
Viewing a thread - How many BTUs to heat shop... (27) Posted 9/29/2018 07:20 (#7015234 - in reply to #7014692)
Subject: RE: How many BTUs to heat shop...

NE Mo

Just a comment for the comments below.

Hot air near the ceiling, and cold at the floor. Many use a fan on the ceiling, ----takes up space for equipment. We have been using a fan on the floor to push cooler air to the ceiling, and force warm air down. Works welll

twraska
Viewing a thread - How many BTUs to heat shop... (30)
Viewing a thread - How many BTUs to heat shop... (31) Posted 9/29/2018 07:33 (#7015256 - in reply to #7014692)
Subject: RE: How many BTUs to heat shop...

Wallis, TX

FYI, some tube heaters can be fairly close to combustibles. My Reverberray (sp) are ok being only 2’ from wood and can be mounted against a wall at a 45 degree angle pointed inward. They are great for keeping tools from sweating.
sdPete
Viewing a thread - How many BTUs to heat shop... (34)
Viewing a thread - How many BTUs to heat shop... (35) Posted 9/29/2018 08:21 (#7015342 - in reply to #7015048)
Subject: RE: How many BTUs to heat shop...

Viewing a thread - How many BTUs to heat shop... (36)
Beresford SD

Seems a lot of overkill in this group. Here. .. a 40 X 50 insulated steel shop 17' sidewalls with a ceiling fan, have a 30,000 btu hanging unit which does fine. It runs about continuous down below zero so heat is steady then.
Viewing a thread - How many BTUs to heat shop... (2024)

FAQs

How many Btu's to heat a shop? ›

For example, a 300 square foot room typically requires 7,000 BTUs to maintain a comfortable temperature, while a 1,000 square foot room requires 18,000 BTUs. A simple formula to determine your heating needs is: (desired temperature change) x (cubic feet of space) x . 133 = BTUs needed per hour.

How many BTUs to heat a 2400 sq ft shop? ›

2,100-square-foot home would take between 65,000 and 125,000 BTUs. 2,400-square-foot homes would take between 75,000 and 145,000 BTUs.

How do you size a unit heater for a shop? ›

Measure the height, length and width of each area you want to heat. Now take and multiply these numbers to obtain the cubic feet. Write down the temperature you want to maintain. Check and see what the lowest area temperature is.

How many BTU for a 400 sq ft garage? ›

Size and Ceiling Height
Area To Be Cooled (square feet)Capacity Needed (BTUs per hour)
400 to 45010,000
450 to 55012,000
550 to 70014,000
700 to 1,00018,000
10 more rows

How many BTU do I need for a 2000 square foot shop? ›

Calculate cooling capacity: You can use a rule of thumb that suggests around 20 BTUs per square foot of space to get an idea of how much cooling capacity you need. Multiply the room's square footage by 20 to get a basic estimate of the required cooling capacity.

How many BTU do I need to heat a 1500 square foot shop? ›

Why Does Furnace Size Matter?
Home SizeFurnace BTUCentral AC Unit Size
1,200 sq. ft50,000 BTU1.5 to 2 tons
1,200 to 1,500 sq. ft55,000 BTU2 tons
1,500 to 1,800 sq. ft60,000 BTU2.5 tons
1,800 to 2,500 sq. ft70,000 BTU2.5 to 3 tons
1 more row

How many BTU do I need for a 2500 square foot shop? ›

The BTU Formula
Room/Area SizeBTU CapacityType
1,500 sq ft68,000-82,000 BTUAverage Home
2,000 sq ft90,000-110,000 BTUGuest House
2,500 sq ft113,000-137,000 BTULarge Home
3,000 sq ft135,000-165,000 BTUOne Zone – Large Home
4 more rows
Dec 6, 2021

How many BTU do I need for a 1200 square foot shop? ›

As a basic rule, the figure will be between 30 and 60 BTUs per square foot.

How many BTU for a 1200 sq ft garage? ›

operate at 20 BTUs to 30 BTUs per square footage. However, these being ballpark estimates, you should confirm accurate cubic feet of cold air in your region and multiply that by the desired warmth in temperature.

What size heater for a 30x30 garage? ›

5,000–10,000 BTUs: Suitable for small garages or workshops (up to 300 square feet) and ideal for spot heating or maintaining a moderate temperature in a limited space. 10,000–20,000 BTUs: Appropriate for medium-sized garages (300 to 600 square feet) and provides more substantial heating capacity for improved coverage.

What is the rule of thumb for sizing unit heaters? ›

The minimum BTU a unit heater would need to have to properly cover the space would be 25,000. Another rule of thumb you can use to calculate BTU that is even simpler is 20 BTU per 1 square foot. Use this in cases where getting measurements or determining insulation may be more difficult.

What type of heater is best to heat a garage? ›

Infrared Heaters

They work well for garages that aren't sufficiently insulated because you're not losing hot air. Pros: Quiet option that can be powered by electricity, propane, or natural gas. Energy-efficient.

What is the rule of thumb for BTU per square foot heating? ›

BTU Calculation Formula

Climate Factor: The climate factor considers whether you need heating or cooling. For heating, use a factor of 20 BTUs per square foot, while cooling requires 25 BTUs per square foot. Insulation Factor: Assess the insulation quality of your space.

Is 12000 BTU enough for 400 sq ft? ›

400 – 450 sq. feet: 10,000 BTUs. 450 – 550 sq. feet: 12,000 BTUs.

Is 12000 BTU enough for 500 sq ft? ›

As a guide, consider 5,000-BTU models for rooms 150 square feet or smaller, 8,000 BTUs for medium-size rooms (340 square feet), and 12,000 to 14,000-BTU models for rooms with square footage from 550 to 800. Having the correct power is imperative.

How many BTUs do I need to heat a 30x30 shop? ›

A good BTU per square foot heating rule of thumb is to look up which climate zone your property is in and then use the following table as a starting point for your recommended BTU per square foot heating value: Zone 1: 30-35 BTU per square foot. Zone 2: 35-40 BTU per square foot. Zone 3: 40-45 BTU per square foot.

How many BTUs to heat a 900 sq ft garage? ›

For a 1 car garage with 200 sq ft to 300 sq ft, the estimated heater size is 15,000 to 25,000 BTUs. For a 2 car garage with 500 sq ft to 700 sq ft, the estimated heater size is 30,000 to 45,000 BTUs. For a 3 car garage with 750 sq ft to 900 sq ft, the estimated heater size is 45,000 to 55,000 BTUs.

How many BTU per square foot for commercial heat? ›

They will then calculate the BTU by dividing the space (in square feet) by 500 and then multiplying its answer by 12,000. They will also add approximately 380 BTU for each person in the space, 1,000 BTU for each window, and 1,200 BTU for each kitchen.

How many BTU per square foot for commercial building heating? ›

Size Your Commercial HVAC System in Five Steps

Divide the square footage area by 500. Multiply the result from Step 2 by 12,000. Add 380 Btu for each building occupant, plus 1,200 Btu for each kitchen and 1,000 Btu for each window in the space.

References

Top Articles
Latest Posts
Article information

Author: Moshe Kshlerin

Last Updated:

Views: 5542

Rating: 4.7 / 5 (77 voted)

Reviews: 84% of readers found this page helpful

Author information

Name: Moshe Kshlerin

Birthday: 1994-01-25

Address: Suite 609 315 Lupita Unions, Ronnieburgh, MI 62697

Phone: +2424755286529

Job: District Education Designer

Hobby: Yoga, Gunsmithing, Singing, 3D printing, Nordic skating, Soapmaking, Juggling

Introduction: My name is Moshe Kshlerin, I am a gleaming, attractive, outstanding, pleasant, delightful, outstanding, famous person who loves writing and wants to share my knowledge and understanding with you.